  • Battery Cable Connection Requirements for MultiPlus-II

    Posted by maxalight on January 14, 2024 at 7:57 pm
    Up
    0
    Down
    ::

    Looking to get the battery cables connected to my MultiPlus-II and I want to ensure I’m using the right specs. Could anyone clarify the cable requirements for me?

    TenTon replied 5 months, 2 weeks ago 3 Members · 2 Replies
  • 2 Replies
  • Tirlant

    Member
    January 15, 2024 at 4:36 am
    Up
    0
    Down
    ::

    Getting the right cable specifications is important to ensuring your MultiPlus-II 230V operates safely and efficiently.

    Here’s what you need to know based on the product’s specifications:

    Battery Capacity: The battery capacity should be chosen according to the model of your MultiPlus-II. For example, a 12/3000/120 model requires a battery capacity ranging from 400-1200 Ah.

    DC Fuse: The recommended DC fuse size is related to the inverter model. For instance, the same 12/3000/120 model should have a 400 A fuse.

    Cable Cross-Section:

    • For cable runs between 0 – 5 meters, a cross-section of 2x 50 mm² is recommended for a 12/3000/120 model, while a 24/5000/120 model would require 2x 50 mm² as well.
    • For cable runs between 5 – 10 meters, you should increase the cross-section to 2x 70 mm² for the 12/3000/120 model and to 2x 70 mm² for the 24/5000/120 model.

    Cable Material and Rating: The DC cables should be made of copper and rated for 90ºC (194ºF) to withstand high temperatures.

    Connection Terminals: Ensure that the cables are properly attached to the + and – connection terminals, with secure and clean connections to prevent any resistance or power loss.

  • TenTon

    Member
    January 15, 2024 at 5:08 am
    Up
    0
    Down
    ::

    Here’s a detailed list of battery cable specifications for various MultiPlus-II models as per the table from the manual:

    Victron Multiplus II – 12/3000/120:

    • Recommended battery capacity: 400-1200 Ah

    • Recommended DC fuse: 400 A

    • Recommended cable cross-section for 0 – 5 m: 2x 50 mm²

    • Recommended cable cross-section for 5 – 10 m: 2x 70 mm²

    Victron Multiplus II – 24/3000/70:

    • Recommended battery capacity: 200-700 Ah

    • Recommended DC fuse: 300 A

    • Recommended cable cross-section for 0 – 5 m: 50 mm²

    • Recommended cable cross-section for 5 – 10 m: 95 mm²

    Victron Multiplus II – 48/3000/35:

    • Recommended battery capacity: 100-400 Ah

    • Recommended DC fuse: 125 A

    • Recommended cable cross-section for 0 – 5 m: 35 mm²

    • Recommended cable cross-section for 5 – 10 m: 70 mm²

    Victron Multiplus II – 24/5000/120:

    • Recommended battery capacity: 400-1400 Ah

    • Recommended DC fuse: 400 A

    • Recommended cable cross-section for 0 – 5 m: 2x 50 mm²

    • Recommended cable cross-section for 5 – 10 m: 2x 70 mm²

    Victron Multiplus II – 48/5000/70:

    • Recommended battery capacity: 200-800 Ah

    • Recommended DC fuse: 300 A

    • Recommended cable cross-section for 0 – 5 m: 70 mm²

    • Recommended cable cross-section for 5 – 10 m: 120 mm²

    Victron Multiplus II – 48/8000/110:

    • Recommended battery capacity: 200-800 Ah

    • Recommended DC fuse: 300 A

    • Recommended cable cross-section for 0 – 5 m: 2x 50 mm²

    • Recommended cable cross-section for 5 – 10 m: 2x 70 mm²

    Victron Multiplus II – 48/10000/140:

    • Recommended battery capacity: 250-1000 Ah

    • Recommended DC fuse: 400 A

    • Recommended cable cross-section for 0 – 5 m: 2x 50 mm²

    • Recommended cable cross-section for 5 – 10 m: 2x 70 mm²

    NOTES:

    • “2x” means two positive and two negative cables.

    • Do not locate battery cables in a closed conduit.

    Make sure to select the specifications corresponding to the exact model of your MultiPlus-II. Proper sizing and fusing of battery cables are crucial for safety and performance.

    Always ensure connections are secure and use the recommended cable gauge to support the required current draw.