How to connect the AC input and outputs for the MultiPlus-II 230V?
Posted by Grippe on January 15, 2024 at 4:40 am::I have a MultiPlus-II 230V and need some guidance on how to properly connect the AC input and outputs without making any mistakes. Can you outline the steps for me?
Arannis replied 1 year, 3 months ago 2 Members · 1 Reply -
1 Reply
-
36 XP
68 Honor
::It’s important to connect your AC input and outputs correctly to ensure the MultiPlus-II 230V functions safely and effectively.
Here’s how to do it:
Identifying AC Terminal Blocks:
-
Locate the AC terminal blocks on the printed circuit board. You’ll find these detailed in Appendix A of the manual.
AC Input Connection (‘AC-in’):
-
Connect the AC input cable to the terminal block labeled ‘AC-in’.
-
Connect the wires from left to right in the order of “N” for Neutral, “PE” for Protective Earth, and “L” for Phase.
-
Ensure not to invert the neutral and phase wires when making these connections.
AC Input Protection: The AC input must be protected by a correctly rated fuse or magnetic circuit breaker:
-
32 A for the 3 kVA model
-
50 A for the 5 kVA model
-
100 A for the 8 kVA and 10 kVA models
-
Size the cable cross-section accordingly, and if your input AC supply is rated lower, downsize the fuse or circuit breaker to match.
AC Output Connection (‘AC-out-1’):
-
The AC output cable can be directly connected to the terminal block ‘AC-out’.
-
Connect the wires from left to right in the order of “N” for Neutral, “PE” for Protective Earth, and “L” for Phase.
-
Include an earth leakage circuit breaker and a fuse or circuit breaker rated for the expected load in series with the output.
-
Size the cable cross-section to accommodate the potential combined output of up to 45 A (the sum of a 32 A input current and a 13 A contribution from PowerAssist).
AC Secondary Output (‘AC-out-2’):
-
This output is used for loads that should only operate when AC power is available on ‘AC-in-1’, such as electric boilers or air conditioners.
-
Connect the secondary loads to ‘AC-out-2’.
-
These loads will be disconnected during battery operation and reconnected after a 2-minute delay once AC power is restored on ‘AC-in-1’ to allow any generator to stabilize.
-