  • How to connect the AC input and outputs for the MultiPlus-II 230V?

    Posted by Grippe on January 15, 2024 at 4:40 am
    Up
    0
    Down
    ::

    I have a MultiPlus-II 230V and need some guidance on how to properly connect the AC input and outputs without making any mistakes. Can you outline the steps for me?

    Arannis replied 5 months, 2 weeks ago 2 Members · 1 Reply
  • 1 Reply
  • Arannis

    Member
    January 15, 2024 at 5:20 am
    Up
    0
    Down
    ::

    It’s important to connect your AC input and outputs correctly to ensure the MultiPlus-II 230V functions safely and effectively.

    Here’s how to do it:

    Identifying AC Terminal Blocks:

    • Locate the AC terminal blocks on the printed circuit board. You’ll find these detailed in Appendix A of the manual.

    AC Input Connection (‘AC-in’):

    • Connect the AC input cable to the terminal block labeled ‘AC-in’.

    • Connect the wires from left to right in the order of “N” for Neutral, “PE” for Protective Earth, and “L” for Phase.

    • Ensure not to invert the neutral and phase wires when making these connections.

    AC Input Protection: The AC input must be protected by a correctly rated fuse or magnetic circuit breaker:

    • 32 A for the 3 kVA model

    • 50 A for the 5 kVA model

    • 100 A for the 8 kVA and 10 kVA models

    • Size the cable cross-section accordingly, and if your input AC supply is rated lower, downsize the fuse or circuit breaker to match.

    AC Output Connection (‘AC-out-1’):

    • The AC output cable can be directly connected to the terminal block ‘AC-out’.

    • Connect the wires from left to right in the order of “N” for Neutral, “PE” for Protective Earth, and “L” for Phase.

    • Include an earth leakage circuit breaker and a fuse or circuit breaker rated for the expected load in series with the output.

    • Size the cable cross-section to accommodate the potential combined output of up to 45 A (the sum of a 32 A input current and a 13 A contribution from PowerAssist).

    AC Secondary Output (‘AC-out-2’):

    • This output is used for loads that should only operate when AC power is available on ‘AC-in-1’, such as electric boilers or air conditioners.

    • Connect the secondary loads to ‘AC-out-2’.

    • These loads will be disconnected during battery operation and reconnected after a 2-minute delay once AC power is restored on ‘AC-in-1’ to allow any generator to stabilize.