  • What should the AC input protection be for my 5 kVA MultiPlus-II model?

    Posted by Farron on January 14, 2024 at 7:58 pm
    Up
    0
    Down
    ::

    I have a 5 kVA MultiPlus-II and need to know the correct AC input protection. What are the specifications for the fuse or circuit breaker?

    TenTon replied 5 months, 2 weeks ago 3 Members · 2 Replies
  • 2 Replies
  • maleous

    Member
    January 15, 2024 at 4:45 am
    Up
    0
    Down
    ::

    For a 5kVA MultiPlus-II model, your AC input should be protected by a fuse or magnetic circuit breaker rated at 50A or less.

    The cable cross-section must be sized accordingly to handle this protection rating.

    If your input AC supply has a lower rating, you should match the protection device to the lower value to prevent overcurrent situations.

  • TenTon

    Member
    January 15, 2024 at 5:14 am
    Up
    0
    Down
    ::

    Protection Device Rating:

    • The AC input of your 5 kVA MultiPlus-II should be protected by either a fuse or a magnetic circuit breaker.

    • This protective device should be rated at 50A or lower. The choice of a 50A rating takes into account the maximum power that the inverter/charger can draw from the AC source.

    Cable Cross-Section Sizing:

    • The cables used for the AC input connection should have a cross-sectional area that’s adequate to handle the current corresponding to a 50A protection device.

    • This ensures that the cables can carry the current without excessive heating or voltage drop, which is essential for safety and efficiency.

    Matching with AC Supply Rating:

    • If your input AC supply is rated lower than 50A, it’s important to match the rating of your protection device to the supply rating.

    • For example, if your AC supply is rated at 30A, then a 30A fuse or breaker should be used. This is to ensure that the protection device trips appropriately in case of an overload, thereby preventing potential hazards.

    Considerations for Inrush Currents:

    • While the normal operating current might be lower than the breaker rating, the 50A rating provides a buffer for the inrush currents that can occur when the inverter/charger starts up or when large loads are switched on.