What should the AC input protection be for my 5 kVA MultiPlus-II model?
Posted by Farron on January 14, 2024 at 7:58 pm::I have a 5 kVA MultiPlus-II and need to know the correct AC input protection. What are the specifications for the fuse or circuit breaker?
TenTon replied 1 year, 3 months ago 3 Members · 2 Replies -
2 Replies
-
19 XP
30 Honor
::For a 5kVA MultiPlus-II model, your AC input should be protected by a fuse or magnetic circuit breaker rated at 50A or less.
The cable cross-section must be sized accordingly to handle this protection rating.
If your input AC supply has a lower rating, you should match the protection device to the lower value to prevent overcurrent situations.
-
26 XP
36 Honor
::Protection Device Rating:
-
The AC input of your 5 kVA MultiPlus-II should be protected by either a fuse or a magnetic circuit breaker.
-
This protective device should be rated at 50A or lower. The choice of a 50A rating takes into account the maximum power that the inverter/charger can draw from the AC source.
Cable Cross-Section Sizing:
-
The cables used for the AC input connection should have a cross-sectional area that’s adequate to handle the current corresponding to a 50A protection device.
-
This ensures that the cables can carry the current without excessive heating or voltage drop, which is essential for safety and efficiency.
Matching with AC Supply Rating:
-
If your input AC supply is rated lower than 50A, it’s important to match the rating of your protection device to the supply rating.
-
For example, if your AC supply is rated at 30A, then a 30A fuse or breaker should be used. This is to ensure that the protection device trips appropriately in case of an overload, thereby preventing potential hazards.
Considerations for Inrush Currents:
-
While the normal operating current might be lower than the breaker rating, the 50A rating provides a buffer for the inrush currents that can occur when the inverter/charger starts up or when large loads are switched on.
-